preferred config would be to directly hook it up to one server via cable, this server runs apcupsd in master-mode and the other servers are controlled by running their apcupsds in slave-mode.
this seems impossible because
1. when i hook up the serial cable to the ups directly (not to its nmc) the only connection that's possible is "dumb" which supplies only some very basic operations;
2. when i hook up the other serial cable (that came with the device; standard serial plug at one end, stereo-audio-line-plug at the other) to the console port on the nmc, same thing, only dumb connection
3. when i tried a usb-to serial-adapter the ups immediately shut down (crashing all the servers hooked up to it!) on pluging it in so i won't try that again
4. snmp seems not to work; apctest only spits out a lot of empty snmp-stuff ("SEQUENCE INTEGER SEQUENCE OBJECTID" ...) and then
Testing not yet implemented for this UPSTYPE
Code: Select all
apcupsd -b5. with pcnet the same as with snmp happens when running apctest.
Code: Select all
apcupsd -bthe system is amd64 and i tried with sys-power/apcupsd-3.14.8-r1 (amd64) and 3.14.10-r1 (keyworded ~amd64). the apcupsd-manuals never mention specific nmc-models and on the web i only fond references to lower model-numbers, eg ap 9617.
am i doing sth. fundamentall wrong with the configuration of snmp/pcnet? snmp was activated in the webif but i activated it via the console again; (it demands a reboot of the ups but i don't want to tray that durcing server-uptime).
does anybody know how to run this? i really don't want to use the proprietary "power chute software" from apc.
THX for your help!