PostPosted: Thu Jul 28, 2005 12:16 am    Post subject: HOWTO: UPS with Gentoo Linux using NUT with MRTG Statistics Reply with quote

HOWTO: UPS with Gentoo Linux using NUT with MRTG Statistics

1.) Introduction

I use the Mustek Powermust USB 2000VA UPS

This UPS is supported by nut version >= 2.0.1

Important Notice:
I recommend you to use the "powermust" driver, as the "mustek" driver doesn't support 24V
UPSes and then you get as battery.value always 100% charge.
Besides, the "powermust" driver has more features.



2.) Install necessary packages


Code:
emerge nut apache2 mrtg 


Add apache to your default runlevel if you don't have done it yet:

Code:
rc-update add apache2 default 


Notice: If you also have a Mustek UPS it might be necessary to use the ~x86 version of nut
because at the moment the latest stable version of nut in the portage tree is version 2.0.0-r1
and this version of nut doesn't support the Mustek UPS series.
So you might do

Code:
echo "www-apps/nut ~x86" >> /etc/portage/package.keywords 


before merging nut!

If you don't have installed a cron daemon install one, e.g.: emerge vixie-cron



3.) Configure nut

Notice: The following configuration files are adapted for a Mustek UPS, if you use another
UPS you will need to change this files for your UPS!
My UPS is connected to COM1 (/dev/ttyS0).

The configuration files of nut are located under /etc/nut!

Index of ups.conf:

    [server]
    driver = powermust
    port = /dev/ttyS0



Index of upsd.conf:

    ACL all 0.0.0.0/0
    ACL localhost 127.0.0.1/32
    ACCEPT localhost
    REJECT all


Index of upsd.users:

    [admin]
    password = yoursecretpassword
    actions = SET
    instcmds = ALL


    [monuser]
    password = yoursecretpassword
    allowfrom = localhost markus



Index of upsmon.conf:


    RUN_AS_USER root
    MONITOR server@localhost 1 monuser yoursecretpassword master
    MINSUPPLIES 1
    SHUTDOWNCMD "/sbin/shutdown -h +0"
    POLLFREQ 5
    POLLFREQALERT 5
    HOSTSYNC 15
    DEADTIME 15
    POWERDOWNFLAG /etc/killpower
    RBWARNTIME 43200
    NOCOMMWARNTIME 300
    FINALDELAY 5



Index of upssched.conf:

    CMDSCRIPT /usr/local/ups/bin/upssched-cmd



Start the daemons an add them to the default runlevel:

Code:
/etc/init.d/upsd start
/etc.init.d/upsmon start
rc-update add upsd default
rc-update add upsmon default




Test if you are able to check the status of your UPS:


Code:
upsc server@localhost 



You should get a output like this:

    battery.charge: 75.0
    battery.voltage: 25.4
    battery.voltage.nominal: 24.0
    driver.name: powermust
    driver.parameter.port: /dev/ttyS0
    driver.version: 2.0.2
    driver.version.internal: 1.1
    input.voltage: 228.6
    input.voltage.fault: 228.1
    input.voltage.maximum: 234.4
    input.voltage.minimum: 227.6
    output.frequency: 50.1
    output.voltage: 225.7
    output.voltage.target.battery: 220.0
    ups.delay.shutdown: 2
    ups.delay.start: 3
    ups.load: 9.0
    ups.mfr: Mustek
    ups.model: PowerMust
    ups.serial: unknown
    ups.status: OL


Notice: If your ouput is different you might have to need change your mrtg config files - see next chapter!


4.) Configure MRTG


Create the directory /etc/mrtg/ups/:

Code:
mkdirhier /etc/mrtg/ups/ 


Download this tar archive and extract it in this directory: index.tar

Code:
cd /etc/mrtg/ups/
tar xvf index.tar 


Make all *.sh-files executable:
Code:
chmod 755 *.sh 


You might have to adapt this files for your system!


Create the index.html file:

Code:
/usr/bin/indexmaker \
--output=/var/www/localhost/htdocs/ups/index.html \
--title="USV Status" --sort=name --enumerate \
/etc/mrtg/ups/voltage.cfg \
/etc/mrtg/ups/batteryvoltage.cfg \
/etc/mrtg/ups/batterycharge.cfg \
/etc/mrtg/ups/load.cfg \
/etc/mrtg/ups/frequency.cfg \
/etc/mrtg/ups/status.cfg \ 



Create the directory /etc/cron.mrtg an create a file named ups.sh with this content...

    #!/bin/sh
    /usr/bin/mrtg /etc/mrtg/ups/voltage.cfg
    /usr/bin/mrtg /etc/mrtg/ups/batteryvoltage.cfg
    /usr/bin/mrtg /etc/mrtg/ups/batterycharge.cfg
    /usr/bin/mrtg /etc/mrtg/ups/status.cfg
    /usr/bin/mrtg /etc/mrtg/ups/load.cfg
    /usr/bin/mrtg /etc/mrtg/ups/frequency.cfg


... and make it executable:
Code:
 chmod 755 ups.sh 


Execute this script (/etc/cron.mrtg/ups.sh) at least three times (don't care about the warnings)!

Run the command crontab -e and add this line to update the statistics every 5 minutes:

    */5 * * * * /bin/run-parts /etc/cron.mrtg 1> /dev/null



5.) Testing

Now open your web browser and open the page http://yourserver/ups

Your should now see your statistics, here a picture of mine: http://www.layr.at/markus/images/linux/ups/ups.jpg



6.) Sending an email when UPS is offline (Optitional)



I use ssmtp to send my an email via my yahoo account to an another email-address of an ISP
which allows forwarding emails to sms, so I get a sms to my mobile phone when the UPS is offine.

Configure ssmtp (/etc/ssmtp/ssmtp.conf):


    root=youraddress@isp.com
    mailhub=smtp.mail.yahoo.com
    rewriteDomain=yahoo.de
    FromLineOverride=YES


Create a file named upsmail.sh in your home directory (root) with this content...


    if [ "`upsc server@localhost ups.status|grep OL`" == "" ]
    then
    echo "Subject: USV OFFLINE" > /tmp/usv.msg
    echo "" >> /tmp/usv.msg
    upsc server@localhost |grep "battery.charge" >> /tmp/usv.msg
    upsc server@localhost |grep "battery.voltage:" >> /tmp/usv.msg
    upsc server@localhost |grep "input.voltage" |grep "input.voltage:" >> /tmp/usv.msg
    upsc server@localhost |grep "output.voltage" |grep "output.voltage:" >> /tmp/usv.msg
    upsc server@localhost |grep "ups.status" >> /tmp/usv.msg
    cat /tmp/usv.msg | /usr/sbin/ssmtp -au yourusername -ap yourpassword tothisaddress@isp.com
    fi


... and make it executable:
Code:
chmod 755 upsmail.sh 


Run the command
Code:
crontab -e


and add this line to executes this script every 5 minutes:

    */5 * * * * /root/usvmail.sh


Now you should get an email if your UPS is offline, I use the sms.at gateway to send my this emails as sms.


Last edited by tuxian on Thu Jul 26, 2007 6:09 pm; edited 2 times in total
Back to top
View user's profile Send private message
NightDragon
Veteran
Veteran


Joined: 21 Aug 2004
Posts: 1156
Location: Vienna (Austria)

PostPosted: Thu Dec 29, 2005 7:59 pm    Post subject: Reply with quote

Great Howto!!!

Works fine.
But it seems that the tar-Archive is corrupt. The file batterycharge.cfg inside looks like an archive...

Could you post the content of the file? Or please correct the archive.

Thx,
Nighty
_________________
You are the problem too all my solutions ;)
Back to top
View user's profile Send private message
tuxian
l33t
l33t


Joined: 26 Jan 2004
Posts: 766
Location: Austria

PostPosted: Thu Dec 29, 2005 8:37 pm    Post subject: Reply with quote

Thanks for the hint, I corrected the archive.
Back to top
View user's profile Send private message
kensh
n00b
n00b


Joined: 25 Jul 2007
Posts: 9

PostPosted: Wed Jul 25, 2007 3:48 pm    Post subject: Reply with quote

Hello,

I know that's a verry old threat, but anyone have the archive . Link is dead.
Or just a model of config.

Thanks you very much.
Back to top
View user's profile Send private message
tuxian
l33t
l33t


Joined: 26 Jan 2004
Posts: 766
Location: Austria

PostPosted: Wed Jul 25, 2007 4:15 pm    Post subject: Reply with quote

Hello,

I fixed the link.

The name of the driver has changed to megatec (I use sys-power/nut-2.0.5-r2 now).
Back to top
View user's profile Send private message
kensh
n00b
n00b


Joined: 25 Jul 2007
Posts: 9

PostPosted: Thu Jul 26, 2007 2:58 pm    Post subject: Reply with quote

Hello Tuxian,

Thanks you very much for this quickly answer :wink:
Back to top
View user's profile Send private message
sbranz
n00b
n00b


Joined: 03 Jul 2007
Posts: 69

PostPosted: Wed Oct 17, 2007 4:09 pm    Post subject: Reply with quote

hi, it's possible to turn POWER ON when return the electricity?
Back to top
View user's profile Send private message
keyson
l33t
l33t


Joined: 10 Jun 2003
Posts: 830
Location: Sweden

PostPosted: Wed Oct 17, 2007 7:36 pm    Post subject: Reply with quote

Hi sbranz,

You mean that you want the PC to start up after the ups had shutdown and when the line power is restored.

Yes this is possible. You set it in the bios of your pc.
You find someting like "Power State After AC Loss" in the settings.
And you may have "On", "Off", "Last State"

Set it to "last state" because if you have it off and don't want it to start, setting it to
"on" would start the PC after a power loss.

This info is in the doc's of nut also.

But you must have setup nut right so it does a shutdown return on power loss.


Regards
Kjell
Back to top
View user's profile Send private message
sbranz
n00b
n00b


Joined: 03 Jul 2007
Posts: 69

PostPosted: Wed Oct 17, 2007 9:31 pm    Post subject: Reply with quote

OKK tnx a lot ;)
Back to top
View user's profile Send private message
Display posts from previous:   
Reply to topic    Gentoo Forums Forum Index Documentation, Tips & Tricks All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum